In article
<1185291389.380746.57630@w3g2000hsg.googlegroups.com>,
> > > Front evaporator inlet line warm, outlet line warm. Accumulator warm.
> > > Located and replaced front orifice tube, system evac. and reserviced
[quoted text clipped - 20 lines]
>
> Ok, 134a 100% unaltered. useing vaccum pump getting down to 25 inches.
Nowhere near enough vacuum. Not even close. Nada. Zip. Zilch.
> When charging, using set of guages.
So, I take it this means you have no way of actually measuring
the refrigerant by weight. There should be a sticker underhood
that specifies X lbs-X ounces. There is a reason for that.
> I've owned truck since 2000 and
> I've never used sealer or cond.
Okay, that's at least one thing positive.
> Unfamiliar about checking oil in
> system.
Simple. If there is any suspicion about the oil quantity like
loss from a leak or there having been any added via cans of
refrigerant/oil mix, the system needs to be flushed and the
proper quantity of oil added to each component.
> Orifice tube fit snug.
That's good
> The old one had debris on the screen.
Well, there shouldn't be debris on the screen. It came from
something somewhere that is disintegrating.
Are you certain that the replacement orifice tube was the correct
one for R-134?
> The accumulator is original and I had thought about replaceing it but
It should be replaced any time the system is opened, like when
you changed the orifice tube. No exceptions.
> I don't like loading the shotgun and throwing parts at something. I
> appreciate your help. Hope i answered all ?'s.
fivejayz@bellsouth.net - 26 Jul 2007 19:42 GMT
> In article
> <1185291389.380746.57...@w3g2000hsg.googlegroups.com>,
[quoted text clipped - 68 lines]
>
> - Show quoted text -
I was using a set of guages. The max vaccum the guages will go to is
30 in. I held a vaccum for about 30 minutes. The system holds 4 lbs
of refri.
aarcuda69062 - 27 Jul 2007 02:00 GMT
In article
<1185475329.075740.96650@r34g2000hsd.googlegroups.com>,
> I was using a set of guages. The max vaccum the guages will go to is
> 30 in. I held a vaccum for about 30 minutes. The system holds 4 lbs
> of refri.
The reason that the vacuum gauge only goes to 30 inches is
because 29.992 is the maximum (theoretical) vacuum achievable on
earth.
Microns is a unit of measurement that can (for purposes of this
discussion) be applied to pressures below atmospheric (vacuum).
The industry standard for evacuating an automotive AC system is
500 microns.
There are 25,400 microns to one inch of mercury.
If all you're pulling is 25 in.hg. vacuum, you're at over 100,000
microns. My micron gauge considers that to be atmospheric,
The two biggest reasons that sufficient vacuum can't be achieved
are;
1) A leak
2) Moisture
You claim it's holding (rules out a leak) that leaves moisture.
Honestly, at 25 in.hg. one really can't be sure either way.
Even though it's a popular belief that at XX vacuum, water will
boil at X * temperature, boiling isn't necessarily removing.
Sounds like this system is highly contaminated.
fivejayz@bellsouth.net - 27 Jul 2007 13:55 GMT
> In article
> <1185475329.075740.96...@r34g2000hsd.googlegroups.com>,
[quoted text clipped - 27 lines]
>
> Sounds like this system is highly contaminated.
I really appreciate all your help. I'm going to r & r the accumulator
this am and go from there.