> > > 1 - Charge for 24 hours
> > > 2 - Run on batteries until fully discharged & check the time
> > > 3 - Recharge for 24 hours
> > > 4 - Run on batteries until fully discharged & check the time
> > > 5 - Average the run times
> > Uh, do NOT do this at home. In fact, do NOT do this ANYWHERE.
> Whether you do this at home or not is certainly your option, but the
> method described is the accepted method for testing uninterruptible
> power supply battery back-up capacity.
Accepted or not, it is not necessary to waste charge cycles and damage a
battery to test its capacity. Battery capacity is (for some) easily
calculated as is intended load.
> We use it as a matter of course
> during development test and evaluation.
I believe you. I'm sure those that are PAYING for the battery are even less
aware of the unnecessary damage being done than those actually doing it.
> As usual, YMMV
No doubt.
As a >32-year employee of the industry that INVENTED the UPS (telephone), we
would (and have) never run the battery DEAD. I stand by my claim that doing
so is very damaging to the battery. In one case, during a "grid power"
failure, the standby generator failed. After several hours on the battery,
the Central Office Technician shut down the switch BEFORE the battery was
fully discharged. This prevented further damage to the battery and still
allowed for some restart capability when recharging capability was restored.
FWIW - In the telco biz, the switch is powered by the battery full-time while
rectified grid power continually recharges the battery. There is NO
"switchover" to the battery during a grid failure: The battery simply no
longer receives its recharge - hence the standby generator.
JR
> -------------------------------------------------
> Whether you do this at home or not is certainly your option, but the
[quoted text clipped - 4 lines]
> As usual, YMMV
> Mark
That might very well be the way you test batteries, if you cannot avail
yourself of the appropriate equipment. OTOH, the dry cell batteries used in
UPS are entirely different in that they are designed to totally discharge
and will not sulfite as wet cells do. However, each time that battery is
totally discharged its life cycle is also shortened.
Wade