The unit is 30 amp which makes things simple.
The inverter is a cheap one with all that means to it.
I intend to use the inverter far more often than the generator.
I thought that the shore power would be connected to the NO contacts of the
first switch with the generator on those contacts with the second. This way
the shore power trumps everything and the generator trumping the inverter.
The inverter would always be connected through the NC contacts.
Dan
OK - Dan,
> The unit is 30 amp which makes things simple.
Every 30 amp I've seen had been 2 wire. That makes thing much simpler.
> The inverter is a cheap one with all that means to it.
Means it probably does not have a transfer switch in it.
> I intend to use the inverter far more often than the generator.
That really doesn't matter.
> I thought that the shore power would be connected to the NO contacts of the
> first switch with the generator on those contacts with the second.
There aren't really NO and NC contacts. There are default and energized
contacts on automatic transfers and you have to really sure which is
which. On a manual switch, there is common and positions 1 & 2.
Common is always down stream (for lack of a better word), so the load
can only select one supply. That way you can never set switches to
inadvertently power up an unused source.
So - Common of switch 1 is connected to the main panels feed.
Position 1 of Switch 1 is connected to the inverter output(*).
Position 2 of Switch 1 is connected to the common of Switch 2.
Position 1 of Switch 2 is connected to the generator output.
Position 2 of Switch 2 is connected to the shore power cable.
Position 1 is default for an automatic transfer switch
> This way the shore power trumps everything and the generator trumping the inverter.
Ok - You got it.
> The inverter would always be connected through the NC contacts.
>
> Dan
* If you are really slick, you can figure out how to make this switch
turn on the inverter and shut down your converter/charger.
Sometimes for owners with an inverter only (not inverter/charger), I add
a single breaker box for the shore power charger(s) at the common of
switch 2. That way the generator or shore can charge batteries.
If you have any doubt is the hardware selected will suffice, send me the
link and I will read about it and offer an opinion.
Good Luck Guy
Matt Colie (aka Yachtsman's Technical Support)
Dan Listermann - 10 May 2007 14:21 GMT
> * If you are really slick, you can figure out how to make this switch turn
> on the inverter and shut down your converter/charger.
> Sometimes for owners with an inverter only (not inverter/charger), I add a
> single breaker box for the shore power charger(s) at the common of switch
> 2. That way the generator or shore can charge batteries.
I have already done this with a relay from Radio Shack. A toggle switch on
the control panel actuates the 12V relay. The NO contacts are wired in
parallel with the inverters on/off switch. The NC contacts interrupt the
110V line to the converter.