>> > Situation where if AC on low fan, both the high pressure and low
>> > pressure lines froze - frost on both lines. Pretty soon, blowing warm
[quoted text clipped - 19 lines]
> High pressure line = liquid line = the line from the compressor to the
> orifice tube or expansion valve.
That's what doesn't figure. That part should be hot under all conditions
(except compressor off). The section from the valve to the evaporator can be
cooled to frost by flash gas if the system is running full bore. To that
extent, I think the OP was doing the best by focusing on why the compressor
was always engaged.
Mike
User - 02 Oct 2005 04:18 GMT
> > High pressure line = liquid line = the line from the compressor to the
> > orifice tube or expansion valve.
[quoted text clipped - 6 lines]
>
> Mike
If there is frost on the liquid line and the system has the proper
charge then there is a restriction in the line just prior to where the
frost starts that acts like an expansion valve. If it is a model that
has the orfice tube under the hood it's possible for the high side line
to frost when the system charge is low.
Bob

Signature
The goal when driving is to miss the maximum number of objects.
James Sweet - 02 Oct 2005 04:24 GMT
> >> > Situation where if AC on low fan, both the high pressure and low
> >> > pressure lines froze - frost on both lines. Pretty soon, blowing warm
[quoted text clipped - 27 lines]
>
> Mike
Er, I forgot to mention the condenser in there, the line goes from the
compressor to the condenser, and then to the expansion device. The line
between the condenser and expansion device shouldn't be hot, but it should
be a bit warmer than ambient depending on condenser efficiency. If that line
is iced up it can be one of two things, a kink or blockage causing a
pressure drop and some of the refrigerant to boil off in the line rather
than in the evaporator, or the evaporator can be so iced up that the liquid
line ices up nearby just from conduction.